A 3ф load of 3 similar inductive coils, each of resistance 50Ω andinductance 0.34H. The supply voltage is 415v/50Hz. calculate thea) Line current (IL)b) Power factors (P.F.)c) The total power when the load is connected in(a) STAR (c) DELTA CONNECTION

Question

A 3ф load of 3 similar inductive coils, each of resistance 50Ω andinductance 0.34H. The supply voltage is 415v/50Hz. calculate thea) Line current (IL)b) Power factors (P.F.)c) The total power when the load is connected in(a) STAR (c) DELTA CONNECTION

🧐 Not the exact question you are looking for?Go ask a question

Solution

Sure, let's solve this step by step:

a) Line current (IL):

First, we need to calculate the impedance (Z) of one coil. The formula for impedance is Z = √(R^2 + (XL)^2), where R is the resistance and XL is the inductive reactance.

The inductive reactance (XL) can be calculated using the formula XL = 2πfL, where f is the frequency and L is the inductance. So, XL = 2π500.34 = 106.81Ω.

Now, we can calculate the impedance: Z = √(50^2 + 106.81^2) = 116.62Ω.

In a star connection, the line current is equal to the phase current. The phase voltage in a star connection is the line voltage divided by √3. So, the phase voltage is 415/√3 = 239.6V.

The phase current (Iph) can be calculated using Ohm's law: I = V/Z. So, Iph = 239.6/116.62 = 2.05A. Therefore, the line current IL = Iph = 2.05A.

b) Power factor (P.F.):

The power factor is the cosine of the phase angle (θ). The phase angle can be calculated using the formula θ = arctan(XL/R). So, θ = arctan(106.81/50) = 65.05°.

Therefore, the power factor is cos(65.05°) = 0.42 (lagging, because it's an inductive load).

c) The total power:

The total power (P) in a 3-phase system can be calculated using the formula P = √3VlIl*P.F., where Vl is the line voltage, Il is the line current, and P.F. is the power factor.

So, in a star connection, P = √34152.05*0.42 = 600.5W.

In a delta connection, the line current is √3 times the phase current, and the phase voltage is the same as the line voltage. So, the line current is √3*2.05 = 3.55A.

Therefore, the total power in a delta connection is P = √34153.55*0.42 = 1039.5W.

This problem has been solved

Similar Questions

A coil of resistance 10Ω and inductance 140mH is connected in parallel with a 260Ωresistor across a 230V, 50Hz supply. Calculate the following(i) Current in the coil (3 Marks)(ii) Supply current (3 Marks)(iii) Circuit impedance (3 Marks)(iv) Power factor (3 Marks)(v) Power consumed

A balanced star connected load of (2+j3) Ω per phase and a balanced delta-connected load of(6+j6) Ω per phase are connected in parallel to a three phase, 400V, 50Hz supply. Calculate thephase current in each load, the total current in each supply line, the total power supplied and theoverall power factor.

Question 2.(a) A coil of resistance 10Ω and inductance 140mH is connected in parallel with a 260Ωresistor across a 230V, 50Hz supply. Calculate the following(i) Current in the coil and phase angle of this current (4 Marks)(ii) Supply current (4 Marks)(iii) Circuit impedance (3 Marks)(iv) Power factor (3 Marks)(v) Power consumed (3 Marks)(b) Explain what is meant by the term “ Power Factor Correction”. Using a phasor diagramshow the impact of a 47μF capacitor placed in parallel with the coil described above.

A 415-V, 50-Hz supply is applied to a three-phase star-connected balanced load. Each [10]phase has an impedance of R+jX ohms, where R=15 n and X = 13.4 n. Find the(i) phase voltage, f'2(ii) phase current,(iii) line current,(iv) power factor,(v) active power,(vi) reactive power,S,vii) total VA

A 3-phase delta connected load consumes a power of 60kW taking a lagging current of 200 A at a line voltage of 400V, 50 Hz. Find the parameters of each phase. What would be the power consumed if the load where connected in star.

1/3

Upgrade your grade with Knowee

Get personalized homework help. Review tough concepts in more detail, or go deeper into your topic by exploring other relevant questions.