n the Two wattmeter method of measuring power in a balanced three-phase circuit, one wattmeter shows zero and the other positive maximum. The load power factor is ___________
Question
n the Two wattmeter method of measuring power in a balanced three-phase circuit, one wattmeter shows zero and the other positive maximum. The load power factor is ___________
Solution
The load power factor in this case is zero.
Here's the step by step explanation:
-
In a balanced three-phase circuit, the power is measured using two wattmeters.
-
If one wattmeter is reading zero, it means that the phase difference between the current and the voltage in that phase is 90 degrees. This is because the power (P) in any phase is given by P=VIcosθ, where V is the voltage, I is the current, and θ is the phase difference between the voltage and the current. If θ is 90 degrees, cosθ is zero, and hence the power is zero.
-
The power factor (cosθ) is a measure of how effectively the current is being converted into useful work output and it is particularly important in power supply systems. It is defined as the cosine of the angle between the voltage and the current.
-
Therefore, if the power in one phase is zero (as indicated by the zero wattmeter reading), the power factor in that phase is also zero.
Similar Questions
In 3 phase power measurement by two wattmeter method, the reading of one wattmeter is zero. The power factor of load is10.500.80.4
n 3-phase power measurement by two-wattmeter method, the two wattmeters read as W1 = 300 W and W2 = 300 W. Then the load is said to be operating at ________ *Unity power factorLagging power factorZero power factorLeading power facto
A three-phase load is balanced if all the three phases have the samea.impedanceb.power factorc.impedance and power factord.none of the above
Three equal impedances are first connected in delta across a three-phase balanced supply. If the same impedances are connected in star across the same supplya.phase current will be one-thirdb.line current will be one-thirdc.noned.power consumed will be one-third
A 415-V, 50-Hz supply is applied to a three-phase star-connected balanced load. Each [10]phase has an impedance of R+jX ohms, where R=15 n and X = 13.4 n. Find the(i) phase voltage, f'2(ii) phase current,(iii) line current,(iv) power factor,(v) active power,(vi) reactive power,S,vii) total VA