A balanced three phase star connected load of 18 kilo watt taking a leading current of 60 A when connected across a 3 phase 440V, 50Hz supply. Find the values and nature of the load
Question
A balanced three phase star connected load of 18 kilo watt taking a leading current of 60 A when connected across a 3 phase 440V, 50Hz supply. Find the values and nature of the load
Solution
To find the values and nature of the load, we need to calculate the power factor, impedance, resistance, and reactance.
-
Power Factor Calculation: The total power P (in kW) in a 3 phase load is given by the formula: P = √3 * V * I * cos(θ), where V is the line voltage, I is the line current, and cos(θ) is the power factor. We can rearrange this formula to solve for the power factor: cos(θ) = P / (√3 * V * I). Substituting the given values: cos(θ) = 18 / (√3 * 440 * 60) = 0.95. Since the current is leading, the load is inductive, and the power factor is lagging.
-
Impedance Calculation: The impedance Z (in ohms) of the load is given by the formula: Z = V / I, where V is the phase voltage and I is the phase current. In a star connected system, the phase voltage V = V_line / √3 = 440 / √3 = 254 V. The phase current I = I_line = 60 A. Substituting these values into the formula: Z = 254 / 60 = 4.23 ohms.
-
Resistance Calculation: The resistance R (in ohms) of the load is given by the formula: R = Z * cos(θ), where Z is the impedance and cos(θ) is the power factor. Substituting the calculated values: R = 4.23 * 0.95 = 4.02 ohms.
-
Reactance Calculation: The reactance X (in ohms) of the load is given by the formula: X = Z * sin(θ), where Z is the impedance and sin(θ) is the square root of (1 - cos²(θ)). Substituting the calculated values: X = 4.23 * √(1 - 0.95²) = 0.85 ohms.
So, the load has a power factor of 0.95 lagging, an impedance of 4.23 ohms, a resistance of 4.02 ohms, and a reactance of 0.85 ohms. The nature of the load is inductive because the current is leading.
Similar Questions
A balanced star connected load of (2+j3) Ω per phase and a balanced delta-connected load of(6+j6) Ω per phase are connected in parallel to a three phase, 400V, 50Hz supply. Calculate thephase current in each load, the total current in each supply line, the total power supplied and theoverall power factor.
A 3-phase delta connected load consumes a power of 60kW taking a lagging current of 200 A at a line voltage of 400V, 50 Hz. Find the parameters of each phase. What would be the power consumed if the load where connected in star.
A 415-V, 50-Hz supply is applied to a three-phase star-connected balanced load. Each [10]phase has an impedance of R+jX ohms, where R=15 n and X = 13.4 n. Find the(i) phase voltage, f'2(ii) phase current,(iii) line current,(iv) power factor,(v) active power,(vi) reactive power,S,vii) total VA
A balanced three-phase star-connected supply of phase sequence ABC feeds a balancedstar connected load of impedance 5025°Ω in each phase. Phase voltage of Phase A ismeasured to be 24030° V.a) Determine the magnitude and phase of each line current supplied by the source.b) Determine the active power and the reactive power supplied by the source.c) Determine the reactive power requirement of each of the three capacitances,connected in star, to improve the power factor to 0.95 lag.
Three equal impedances are first connected in delta across a three-phase balanced supply. If the same impedances are connected in star across the same supplya.phase current will be one-thirdb.line current will be one-thirdc.noned.power consumed will be one-third