A single Phase 50kVA, 2400/240V, 60Hz distribution transformer is used as a step downtransformer at the load end of a 2400V feeder whose series impedance is (1.0 + j2.0) ohms. Theequivalent series impedance of the transformer is (1.0 + j2.5) ohms referred to the high voltage (i.e.primary) side. The transformer is delivering rated total power at 0.8 power factor lagging, and atrated secondary voltage. Neglecting the transformer excitation current, determine:(a) The voltage at the transformer primary terminals,(b) The voltage at the sending end of the feeder,(c) The real and reactive power delivered to the sending end of the feeder.Work in the Per Unit System, using the transformer ratings as base quantities

Question

A single Phase 50kVA, 2400/240V, 60Hz distribution transformer is used as a step downtransformer at the load end of a 2400V feeder whose series impedance is (1.0 + j2.0) ohms. Theequivalent series impedance of the transformer is (1.0 + j2.5) ohms referred to the high voltage (i.e.primary) side. The transformer is delivering rated total power at 0.8 power factor lagging, and atrated secondary voltage. Neglecting the transformer excitation current, determine:(a) The voltage at the transformer primary terminals,(b) The voltage at the sending end of the feeder,(c) The real and reactive power delivered to the sending end of the feeder.Work in the Per Unit System, using the transformer ratings as base quantities

...expand
🧐 Not the exact question you are looking for?Go ask a question

Solution

To solve this problem, we will use the per unit system and the transformer ratings as base quantities.

(a) The voltage at the transformer primary terminals:

First, we need to calculate the per unit impedance of the transformer and the feeder.

The base impedance (Zbase) on the primary side of the transformer is given by Vbase^2 / Sbase, where Vbase is the base voltage and Sbase is the base power.

So, Zbase = (2400)^2 / 50000 = 115.2 ohms.

The per unit impedance of the transformer (Zpu_t) is then the transformer impedance divided by the base impedance.

So, Zpu_t = (1.0 + j2.5) / 115.2 = 0.0087 + j0.0217.

Similarly, the per unit impedance of the feeder (Zpu_f) is (1.0 + j2.0) / 115.2 = 0.0087 + j0.0174.

The total per unit impedance (Zpu_total) is the sum of Zpu_t and Zpu_f, which is 0.0174 + j0.0391.

The per unit voltage at the primary terminals of the transformer (Vpu_t) is given by 1 - Ipu * Zpu_total, where Ipu is the per unit current.

Since the transformer is delivering rated total power at 0.8 power factor lagging, Ipu = 1 * 0.8 - j1 * 0.6.

So, Vpu_t = 1 - (0.8 - j0.6) * (0.0174 + j0.0391) = 0.970 - j0.027.

The actual voltage at the transformer primary terminals is then Vpu_t * Vbase = (0.970 - j0.027) * 2400 = 2328 - j64.8 V.

(b) The voltage at the sending end of the feeder:

The per unit voltage at the sending end of the feeder (Vpu_s) is given by Vpu_t + Ipu * Zpu_f.

So, Vpu_s = (0.970 - j0.027) + (0.8 - j0.6) * (0.0087 + j0.0174) = 0.977 - j0.044.

The actual voltage at the sending end of the feeder is then Vpu_s * Vbase = (0.977 - j0.044) * 2400 = 2344.8 - j105.6 V.

(c) The real and reactive power delivered to the sending end of the feeder:

The per unit power (Spu) is given by Vpu_s * Ipu*.

So, Spu = (0.977 - j0.044) * (0.8 - j0.6) = 0.7816 - j0.5864.

The actual power is then Spu * Sbase = (0.7816 - j0.5864) * 50000 = 39080 - j29320 VA.

So, the real power is 39080 W and the reactive power is -29320 VAR.

This problem has been solved

Similar Questions

6. Multi-Voltage Level SystemA power system includes a generator (500 MVA, 13.8 kV, X'' = 0.2 pu), a transformer (500MVA, 13.8/138 kV, Z = 0.1 pu), and a transmission line (Z = 0.02 + j0.1 pu on 138 kV, 500MVA base). A load of 450 MW at 0.9 power factor lagging is connected at the end of thetransmission line.a. Convert all impedances to a common base of 500 MVA, 13.8 kV.b. Calculate the per-unit voltage at the load bus.

The core loss of a 5KVA single phase transformer with normal voltage applied to the primary is 74 watts. The maximum efficiency occurs at 70% of full-load KVA. What is the full load efficiency of the transformer at untiy power factor?

An 10000/100V, 50 Hz, single phase transformer has an exciting current of 0.8 A and a core loss of 400 W when its HV side is energized at rated voltage. The core loss component of the existing current is ?

A transformer has 400 turns on the primary and 100 turns on the secondary. If 120 volts AC are applied across the primarywindings, calculate the voltage induced in the secondary.

Question 2List three functions which a transformer may perform in an electrical circuit. [3 marks]A 10kVA, 50 Hz distribution transformer has 600 turns in the primary and 120 turns in thesecondary. The primary and secondary resistances are r1 = 0.2 Ω and r 2 = 0.02 Ω respectively,and the corresponding leakage reactances are Xl1 = 1.0 Ω, and Xl2 = 0.04 Ω respectively. Thesupply voltage is 1100V.Calculate(a) The equivalent impedance, resistance and reactance, referring all quantities to thehigh voltage (primary) side; [6 marks](b) The secondary terminal voltage for full load having a power factor of 0.7 lagging;Draw the phasor diagram; [7 marks](c) The regulation in (b) [4 marks]2130310310

1/2

Upgrade your grade with Knowee

Get personalized homework help. Review tough concepts in more detail, or go deeper into your topic by exploring other relevant questions.